Managing PV + battery system
« on: September 20, 2017, 01:43:01 PM »
Hello,
At work, we just started a PV (20 kWp) + Battery (15kWh) system on a building with 4 appartments  that have heatpump heating (well, appartments are only half full yet), and I have to say that it works better than what I expected. Even now mid September, on rainy days, we have enough electricity until like midnight (heating is only needed for sanitary water yet).
A lot of sun doesn't help much because batteries are full around noon, so we start to use extra tips to use PV electricity in excess.
I started the "what to do with PV electricity in excess topics http://forum.arctic-sea-ice.net/index.php/topic,2076.0.html when the conception of the regulation was underway. It seems to work fine.
Since most ways of using excess PV electricity are not so efficient or mean higher energy loss (an overheated boiler has over average heat loss), I decided to stop any not needed electricity use during peak hours (around noon and after 16h) in order to support the local electricity network. The idea is also to have some experiences for future smart meters and regulations that might come with them.
Does any body has experiences in that area, some good tips...
Thanks,
Etienne

etienne

  • Nilas ice
  • Posts: 2043
    • View Profile
    • About energy
  • Liked: 309
  • Likes Given: 23
Re: Managing PV + battery system
« Reply #1 on: September 20, 2017, 06:37:52 PM »
Maybe I should add that the systems installed to use PV power in excess aim to anticipate needs of energy during the time where there is no sun. For example when I overheat sanitary water with PV power, I anticipate the next heating process that might happen when no PV power is available. It's not a waste of energy, the waste comes only from the increasing losses due to higher temperature in the storage tank.

We will have a winter and a summer configuration, because for example during the winter, it could be interesting to heat sanitary water at night when electricity is abundant on the network.

oren

  • First-year ice
  • Posts: 9799
    • View Profile
  • Liked: 3582
  • Likes Given: 3914
Re: Managing PV + battery system
« Reply #2 on: September 21, 2017, 10:49:18 PM »
Nice project etienne. I envy you. Nothing like real life experience with these things.

Zythryn

  • New ice
  • Posts: 81
    • View Profile
  • Liked: 9
  • Likes Given: 47
Re: Managing PV + battery system
« Reply #3 on: September 22, 2017, 02:19:37 AM »
We have a net-zero setup using PV power.  No battery backup yet, but we are planning to have that installed within two months.
One thought would be to charge an electric car when you have a surplus.  Not sure if you have one available during the afternoon, but that will allow for a good chunk of storage.

GeoffBeacon

  • Frazil ice
  • Posts: 394
    • View Profile
  • Liked: 18
  • Likes Given: 21
Re: Managing PV + battery system
« Reply #4 on: September 22, 2017, 12:50:55 PM »
Etienne

The thinking in your project sounds excellent - I hope the practice is too. Looking forward to results if you monitor the real life situation.

However when you say "appartments are only half full yet" and "charge an electric car" suggests to me that the embodied carbon in building and cars have been ignored.

Do look at Embodied carbon recognised at last.

The Embodied Carbon Task Force of the The Alliance for Sustainable Building Products reported
Quote
–Even before a building is occupied, between 30% – 70% of its lifetime carbon emissions have already been accounted for.
–Embodied carbon makes up the largest proportion of the carbon emissions of a building through its lifetime.
Have I go the carbon impact of building new conventional buildings and making new electric cars wrong?

Green thinking with conventional planning can easily fail.

Perhaps your system could work with low rise wooden buildings with bike transport?
Il faut cultiver notre cité-jardin
The Sustainable Plotlands Association

etienne

  • Nilas ice
  • Posts: 2043
    • View Profile
    • About energy
  • Liked: 309
  • Likes Given: 23
Re: Managing PV + battery system
« Reply #5 on: September 22, 2017, 02:18:41 PM »
The building was finished in July. From 4 owners, only one has fully moved. Two owners are still between their old and new appartment, and the 4th owner is looking for a tenant. So I can't give real conclusions yet.

None of the owners/tenant has an electrical car. Probably in the future. Infrastructure will be easy to install, but is not required yet. The problem with EV and PV is that cars are on professional parking lot during the day.

Carbon calculation is not an issue in this project. Our part of the work is energy management, so we don't have a choice regarding the other aspects. It's nice for us when people are ready to buy batteries because with the actual regulations in Luxembourg, it is a "just for fun" investment. I believe that it will change in the future, but not before 2-3 years.

In the "policy and solution/renewable energy" trend is a nice link from ghoti about what could be done anywhere if the network regulator would be ready (its in the Orkney Islands):
https://www.youtube.com/watch?v=VEh7V9_uIqM&feature=youtu.be
but it requires a lot of work on the network regulator side.
Imagine what would happen if the regulator just says he has too much electricity so it is now 20% cheaper. On the building I manage, I can start 12 kW load just on water and buiding heating, but in each appartment is a washmachine, a dryer... It would create a total breakdown of the electrical network.
The PV/battery management system we have allows us to define different loads that can be started with different priorities. So I guess the network regulator could do the same thing, homes could enroll in a project, define what their extra load could be, and the regulator should be able to start them.
In the Orkney project, they solve that problem using the batteries as variable load. I guess that the end users pay always the same price for electricity, so they won't start all the systems together at the minute where it becomes cheaper. Since the utility company knows the load curve of the house, it is able to fill the batteries whenever network and electricity are available and can empty them when there is no load in the house and electricity is expensive. I guess that there are some additional requirements like heating sanitary water at night.
With the renewable/storage revolution, I believe that utility companies won't make so much money on electricity anymore, but on energy management. It's a new business case.

etienne

  • Nilas ice
  • Posts: 2043
    • View Profile
    • About energy
  • Liked: 309
  • Likes Given: 23
Re: Managing PV + battery system
« Reply #6 on: September 27, 2017, 03:10:00 AM »
We are now preparing the concepts for new houses and it's unbelievable how things have change on the last years. It is now possible to find plug and play solutions for PV electricity use optimisation with a heat pump. And is is cheap (like around 500 EUR). Since suppliers have full control of their systems, the plug and play solutions might be more efficient than what can be done with the normal public interface. Configuration is more complicated, but Microsoft has developped the installation wizard concept, I guess this also works here.
With the batteries dropping costs, I wonder if PV optimisation will be an issue in the future. It will be possible to increase the battery size and optimize energy use, not just PV energy use.
Furthermore, heat pumps are also improving quite a lot, and I guess it will soon be interesting to use them for normal houses (not only highly insulated) if you add a pellet stove to bring enough heat for the winter months.

Jim Hunt

  • First-year ice
  • Posts: 6264
  • Don't Vote NatC or PopCon, Save Lives!
    • View Profile
    • The Arctic sea ice Great White Con
  • Liked: 891
  • Likes Given: 86
Re: Managing PV + battery system
« Reply #7 on: November 22, 2017, 02:40:12 PM »
Hi Etienne,

I think I just asked my "smart meter" question in the wrong thread!

You may wish to peruse this recent article of mine?

http://www.V2G.co.uk/2017/09/evangelising-v2g-in-south-west-england/

The MyEnergi Eddi/Zappi combination may well be of interest in here? Also we're currently attempting to raise funding for a (hopefully!) novel hybrid PV inverter project. Perhaps we should compare notes at some point?
"The most revolutionary thing one can do always is to proclaim loudly what is happening" - Rosa Luxemburg

etienne

  • Nilas ice
  • Posts: 2043
    • View Profile
    • About energy
  • Liked: 309
  • Likes Given: 23
Re: Managing PV + battery system
« Reply #8 on: November 22, 2017, 07:00:41 PM »
Hi Jim,

It's an interesting article. The main problem I see right now is that optimisation is tried on a building level, but a wider area should be considered, at least all the users of the 20kV line that supplies them.
Electricity need at night is lower than during the day, which means that I wouldn't use the battery to load the car at night, but to support house consumption in the morning before the sun goes up. On the building I manage, the absolute peaks are in the morning when coffee machines and water heaters are working. Water heater are related to showers and coffee machines to breakfast. There is also a peak in the evening, but wider and lower (probably higher total consumption, but during more time). Maybe we should have had a bigger warm water storage.
The second point is that the general load curve is higher during the day, so on a global level, PV related batteries could only be loaded when global supply is insured without CO2.
I wonder how smart grid will be able to manage a fair sharing of the incomes related to discharging batteries in the network when electricity demand is high. Same question about who will be able to load his battery with cheap electricity when supply is higher than demand.

Regarding MyEnergi Eddi/Zappi, I have to read more about it. I can't give you an answer yet.

Etienne

Jim Hunt

  • First-year ice
  • Posts: 6264
  • Don't Vote NatC or PopCon, Save Lives!
    • View Profile
    • The Arctic sea ice Great White Con
  • Liked: 891
  • Likes Given: 86
Re: Managing PV + battery system
« Reply #9 on: November 22, 2017, 09:09:41 PM »
A wider area should be considered, at least all the users of the 20kV line that supplies them.

It's funny you should mention that! Agreed, except that here in the UK it's 11 kV.

Quote
Electricity need at night is lower than during the day, which means that I wouldn't use the battery to load the car at night, but to support house consumption in the morning before the sun goes up. On the building I manage, the absolute peaks are in the morning when coffee machines and water heaters are working. Water heater are related to showers and coffee machines to breakfast. There is also a peak in the evening, but wider and lower (probably higher total consumption, but during more time). Maybe we should have had a bigger warm water storage.

The MyEnergi system certainly relies on heating water when all other attempts at self consumption fail.
 
Quote
The second point is that the general load curve is higher during the day, so on a global level, PV related batteries could only be loaded when global supply is insured without CO2.

Not that it's a lot of use to you in Luxembourg, but you might be interested in our open source UK grid carbon intensity app?

http://www.V2G.co.uk/projects/national-grid-carbon-intensity-api/

Today's graph is below.

Quote
I wonder how smart grid will be able to manage a fair sharing of the incomes related to discharging batteries in the network when electricity demand is high. Same question about who will be able to load his battery with cheap electricity when supply is higher than demand.

The $64,000 question! The conventional answer is a fully functional "local energy market", but we're a million miles away from such a thing in the UK.
« Last Edit: November 23, 2017, 12:40:38 AM by Jim Hunt »
"The most revolutionary thing one can do always is to proclaim loudly what is happening" - Rosa Luxemburg

etienne

  • Nilas ice
  • Posts: 2043
    • View Profile
    • About energy
  • Liked: 309
  • Likes Given: 23
Re: Managing PV + battery system
« Reply #10 on: November 22, 2017, 10:52:52 PM »
When I check the datas of my Smappee, I see that I use between 6 and 12 kWh per day.  I guess that the highest power usage was around 10kW, but we didn't pay attention at limiting total power.
This means that with a 5 kWh battery, I really could cut all the peaks of my consumption. I guess this might be a solution for the future :  a battery that fills itself when power is available, and makes sure that I never take more than 4 kW from the network.

sidd

  • First-year ice
  • Posts: 6771
    • View Profile
  • Liked: 1046
  • Likes Given: 0
Re: Managing PV + battery system
« Reply #11 on: November 23, 2017, 12:27:26 AM »
" a battery that fills itself when power is available, and makes sure that I never take more than 4 kW from the network."

Called "peak shaving"  and being used in industrial and commercial settings. A lot of is is thermal store (supercool freezers or make ice when power is cheap) but some is battery based. This is important for thos (usually) large electric customers whose rates are partially basd on peak load.

sidd

Jim Hunt

  • First-year ice
  • Posts: 6264
  • Don't Vote NatC or PopCon, Save Lives!
    • View Profile
    • The Arctic sea ice Great White Con
  • Liked: 891
  • Likes Given: 86
Re: Managing PV + battery system
« Reply #12 on: November 23, 2017, 10:15:21 AM »
For the benefit of Neven (and anybody else who might be interested) this is what my SMETS 1 spec smart meter looks like. Hopefully the SMETS 2 devices due RSN will actually possess some smarts!

The communications module is at the top. WAN is GPRS, when it can get a signal. HAN is ZigBee, which communicates with the mini tablet inside the house, amongst other things.

Thanks in part to the Great British Chancellor of the Exchequer we're currently seeking expressions of interest from anybody in Europe with a suitably smart meter who might be interested in beta testing some novel electric vehicle charging equipment in a few months time.
"The most revolutionary thing one can do always is to proclaim loudly what is happening" - Rosa Luxemburg

etienne

  • Nilas ice
  • Posts: 2043
    • View Profile
    • About energy
  • Liked: 309
  • Likes Given: 23
Re: Managing PV + battery system
« Reply #13 on: November 23, 2017, 10:45:40 PM »
" a battery that fills itself when power is available, and makes sure that I never take more than 4 kW from the network."

Called "peak shaving"  and being used in industrial and commercial settings. A lot of is is thermal store (supercool freezers or make ice when power is cheap) but some is battery based. This is important for thos (usually) large electric customers whose rates are partially basd on peak load.

sidd

Peak shaving as described is much easier to manage in the context of industrial and commercial settings because they usually have an infrastructure managing system and have a wider choice of load to start and stop.
At home, my peak is in the evening (lights on) when the chicken is in the oven and the potatoes + the vegetables in two different pans. Even if I would stop my refrigerator and would make sure that no laundry appliance works at the same time, this wouldn't solve my problem.
To be very honnest, this is not a problem right now, but next year in Luxembourg we will have a proof of concept on a residential building with self consumption of PV electricity where the network costs will be based on the highest peak of the year. In the 2017 context, self consumed eletricity has the same network cost than bought electricity because the network was available to transport it. The building has batteries with an SMA home manager, so it would be nice to use it for peak shaving. We asked for it and got more specific questions about our needs, so maybe they will offer the functionnality sometimes in the future.

Neven

  • Administrator
  • First-year ice
  • Posts: 9433
    • View Profile
    • Arctic Sea Ice Blog
  • Liked: 1333
  • Likes Given: 617
Re: Managing PV + battery system
« Reply #14 on: November 24, 2017, 12:10:31 AM »
Jim, does 'intimate communications hub' mean you have to report the numbers without any clothes on via webcam?  ;)

Sorry for all the bad jokes.

I'll go and see what kind of a meter my meter actually is.
The enemy is within
Don't confuse me with him

E. Smith

Jim Hunt

  • First-year ice
  • Posts: 6264
  • Don't Vote NatC or PopCon, Save Lives!
    • View Profile
    • The Arctic sea ice Great White Con
  • Liked: 891
  • Likes Given: 86
Re: Managing PV + battery system
« Reply #15 on: November 24, 2017, 09:27:39 AM »
Good morning Neven. Actually I'm quite partial to "bad jokes" myself. In fact I have one of my very own to share with you!

Perhaps you and any other renewable energy enthusiasts in the house might wish to bookmark the Twitter thread that I just recommended to Professor Richard Betts of the UK Met Office?

https://twitter.com/jim_hunt/status/933970006106411009
« Last Edit: November 24, 2017, 11:02:04 AM by Jim Hunt »
"The most revolutionary thing one can do always is to proclaim loudly what is happening" - Rosa Luxemburg

etienne

  • Nilas ice
  • Posts: 2043
    • View Profile
    • About energy
  • Liked: 309
  • Likes Given: 23
Re: Managing PV + battery system
« Reply #16 on: November 25, 2017, 03:54:10 PM »
When I look at my consumption graph (5 minutes average), shaving peaks above 1,5 kW would require almost no battery power, but it would require a high power inverter and a fast discharging batteries.

ghoti

  • Grease ice
  • Posts: 767
    • View Profile
  • Liked: 12
  • Likes Given: 15
Re: Managing PV + battery system
« Reply #17 on: November 25, 2017, 05:19:36 PM »
Quote
When I look at my consumption graph (5 minutes average), shaving peaks above 1,5 kW would require almost no battery power, but it would require a high power inverter and a fast discharging batteries.
That looks to be readily available. The Tesla Powerwall provides 5kW steady output and 7kW peak output. It has the inverter built in. I would be surprised if similar wasn't also available from Sonnen and other battery providers.

sidd

  • First-year ice
  • Posts: 6771
    • View Profile
  • Liked: 1046
  • Likes Given: 0
Re: Managing PV + battery system
« Reply #18 on: November 25, 2017, 09:26:54 PM »
"When I look at my consumption graph (5 minutes average), shaving peaks above 1,5 kW would require almost no battery power, but it would require a high power inverter and a fast discharging batteries."

Could you integrate the peaks above 1.5kkW and estimate averages/medians/peak energy requirements in KwH as well ? I ask because this might be an application for a capacitor bank coupled to batteries.

sidd

Jim Hunt

  • First-year ice
  • Posts: 6264
  • Don't Vote NatC or PopCon, Save Lives!
    • View Profile
    • The Arctic sea ice Great White Con
  • Liked: 891
  • Likes Given: 86
Re: Managing PV + battery system
« Reply #19 on: November 25, 2017, 10:52:03 PM »
The Tesla Powerwall provides 5kW steady output and 7kW peak output. It has the inverter built in. I would be surprised if similar wasn't also available from Sonnen and other battery providers.

Similar devices are indeed available from a variety of other battery providers. Here are just a few:

http://www.v2g.co.uk/2015/06/is-distributed-energy-storage-on-ofgems-roadmap/

Scroll to the bottom to see them. I'm late to this party I'm afraid, so if I may enquire:

Etienne - Do you have high voltage batteries like the Powerwall (et al!)
"The most revolutionary thing one can do always is to proclaim loudly what is happening" - Rosa Luxemburg

etienne

  • Nilas ice
  • Posts: 2043
    • View Profile
    • About energy
  • Liked: 309
  • Likes Given: 23
Re: Managing PV + battery system
« Reply #20 on: November 26, 2017, 12:47:02 PM »

Could you integrate the peaks above 1.5kkW and estimate averages/medians/peak energy requirements in KwH as well ? I ask because this might be an application for a capacitor bank coupled to batteries.

sidd

Yes, but not today. Maybe middle of next week.

Etienne

etienne

  • Nilas ice
  • Posts: 2043
    • View Profile
    • About energy
  • Liked: 309
  • Likes Given: 23
Re: Managing PV + battery system
« Reply #21 on: November 26, 2017, 10:12:58 PM »
Well, here are some first results.

Average power usage is around 400 W

I have a scenario where I load batteries at night (24h time frame):

I need 1.9 kWh to shave peaks above 1.5 kW, and 0.9 kWh to shave above 2 kW.
If I remove the day where my wife used the dryer (clothes), the values are 1.2 kWh and 0.6 kWh.

There is also a 4 hours scenario (close to a V2G configuration)

I need 1.1 kWh to stay under 1.5 kW and 0.6 kWh to stay under 2kW.
Here again, if I remove the dryer's day, it is 0.35 kWh and 0.7 kWh.

Here, I still need to check if power usage goes down enough to allow battery charging before the next peak.


Of course, the needed power is quite important, like 7 kW (Smappee also shows real time values, but doesn't keep them).

sidd

  • First-year ice
  • Posts: 6771
    • View Profile
  • Liked: 1046
  • Likes Given: 0
Re: Managing PV + battery system
« Reply #22 on: November 27, 2017, 01:30:39 AM »
Capacitors capable of holding kilowatthours are monstrous, gotto go with battery. 2wH is fairly small for batteries. That said, capacitors can help with motor start loads, but handle with care, you may get overheating of motor coils if you do it wrong.

sidd

TerryM

  • First-year ice
  • Posts: 6002
    • View Profile
  • Liked: 893
  • Likes Given: 5
Re: Managing PV + battery system
« Reply #23 on: November 27, 2017, 02:17:30 PM »
Quick start / hard start kits on AC/Heat Pumps help with start loads, but resistant heating for clothes driers can be a problem. In low humidity environments disconnecting the heaters and siting the drier outside works well. In winter venting a conventional dryer's heat back through the building cuts heater usage.
Caution, may not work efficiently away from desert regions. 8)


Terry

etienne

  • Nilas ice
  • Posts: 2043
    • View Profile
    • About energy
  • Liked: 309
  • Likes Given: 23
Re: Managing PV + battery system
« Reply #24 on: November 27, 2017, 09:04:33 PM »
Hello,

Here are the last values.

The median value of my electrical consumption is 290 W, much under the average that was 390 W.
This is not a surprise because peaks are very thin.

The 4 hours scenario works, it means that I have always enough time with low power to reload the battery within the 4 hours following a peak, even if I want to stay under 1500 W of maximum power. That's good news for the V2G concept.

Best regards,

Etienne

Sebastian Jones

  • Grease ice
  • Posts: 716
    • View Profile
  • Liked: 214
  • Likes Given: 158
Re: Managing PV + battery system
« Reply #25 on: November 27, 2017, 09:46:14 PM »
resistant heating for clothes driers can be a problem. In low humidity environments disconnecting the heaters and siting the drier outside works well. In winter venting a conventional dryer's heat back through the building cuts heater usage.
Caution, may not work efficiently away from desert regions. 8)


Terry
If one is seriously considering powering one's house with a PV + battery system, the very first thing to do is get rid of a clothes dryer. Clothes dry perfectly well hanging up, inside or out.

etienne

  • Nilas ice
  • Posts: 2043
    • View Profile
    • About energy
  • Liked: 309
  • Likes Given: 23
Re: Managing PV + battery system
« Reply #26 on: November 27, 2017, 09:50:41 PM »
Hello,

Here is my 4 hours scenario using the data of the day with the highest requirements. Battery need is 1,1 kWh. edit : 600 Wh, see comment below

I only use the dryer 4 to 5 times a year, so I think it's no use to buy a new one.

Best regards,

Etienne
« Last Edit: January 07, 2018, 03:49:27 PM by etienne »

TerryM

  • First-year ice
  • Posts: 6002
    • View Profile
  • Liked: 893
  • Likes Given: 5
Re: Managing PV + battery system
« Reply #27 on: November 29, 2017, 10:12:27 PM »
resistant heating for clothes driers can be a problem. In low humidity environments disconnecting the heaters and siting the drier outside works well. In winter venting a conventional dryer's heat back through the building cuts heater usage.
Caution, may not work efficiently away from desert regions. 8)


Terry
If one is seriously considering powering one's house with a PV + battery system, the very first thing to do is get rid of a clothes dryer. Clothes dry perfectly well hanging up, inside or out.
Undoubtedly true.
I was simply listing a few of the things I used when living in the Mojave desert. I think the solar preheater for the hot water system, and shunting much of my A/C's heat load into my swimming pool were probably the most successful ways that I avoided a high energy bill.
Living in a more forgiving climate presents it's own problems.
Terry

etienne

  • Nilas ice
  • Posts: 2043
    • View Profile
    • About energy
  • Liked: 309
  • Likes Given: 23
Re: Managing PV + battery system
« Reply #28 on: January 01, 2018, 08:48:58 PM »
Hello,

Here is my V2G graph for Christmas time (December 24th, 25th, 26th).

This time, I need a 2 kWh battery for a peak shaving at 1500W. edit : 1,6 kWh, see comment below

Datas are always 5 minutes average.

Best regards,

Etienne
« Last Edit: January 07, 2018, 03:49:13 PM by etienne »

etienne

  • Nilas ice
  • Posts: 2043
    • View Profile
    • About energy
  • Liked: 309
  • Likes Given: 23
Re: Managing PV + battery system
« Reply #29 on: January 07, 2018, 03:47:16 PM »
I made a little mistake in my calculations. During Christmas time, 1,6 kWh battery would have been enough for peak shaving at 1,5 kW, and during the first example, 0,6 kWh would have been enough.

First values where how much energy above 1,5 kW is used during 4 hours, but I didn't deduct the loading possibilities that where available during that time.

New values are, knowing that my batteries don't loose any energy in loading and unloading, that the system is very fast to load the batteries each time that power usage goes under 1,5 kW, this is the battery power I need.

I tried with only 80% efficiency, but I got the same values because times between peaks is long enough to reload the batteries even with 80% efficiency.

gerontocrat

  • Multi-year ice
  • Posts: 20288
    • View Profile
  • Liked: 5277
  • Likes Given: 69
Re: Managing PV + battery system
« Reply #30 on: January 07, 2018, 04:05:49 PM »
It is a very good idea to use 80% of theoretical performance in system design- or even less for critical systems, as assuming systems never degrade in performance is a recipe for a screw-up.
"Para a Causa do Povo a Luta Continua!"
"And that's all I'm going to say about that". Forrest Gump
"Damn, I wanted to see what happened next" (Epitaph)

A-Team

  • Young ice
  • Posts: 2977
    • View Profile
  • Liked: 944
  • Likes Given: 35
Re: Managing PV + battery system
« Reply #31 on: January 07, 2018, 04:22:09 PM »
Excellent posts, Etienne.

Today I climb the mesquite tree to prune off the top and one side as it is shading our rooftop panels with the low winter sun angle. It will grow back worse than ever though. Tomorrow the guys come out to change the bracket legs a little because the first row of panels is shading the second from 2:00 pm on, again a winter problem. We are at 32.2° N.

It doesn't matter really because as just a residence, we are close to net-zero and would be paid little by the utility for giving them excess energy because of how they lobbied bribed the state rate commission.

Clothes dryer? I just sling the wet laundry over the back of the patio furniture. It is bone dry in an hour. Like Southern California, we have been 3-4ºC over climate for months now. It has not rained since late July. Biggest issue is the cute little squirrels (Ammospermophilus harrisii). They come on the deck and chew up socks, cotton clothing and even shoe laces to line their nests.

ghoti

  • Grease ice
  • Posts: 767
    • View Profile
  • Liked: 12
  • Likes Given: 15
Re: Managing PV + battery system
« Reply #32 on: January 07, 2018, 06:53:39 PM »
Quote
Biggest issue is the cute little squirrels
Watch for them nesting under your PV panels and chewing on the wires. Had a family with 4 babies defeat the metal mesh around one of my panels this year - the wiring was chewed but not destoryed. After i poked around the mom carried the babies off to another location.

etienne

  • Nilas ice
  • Posts: 2043
    • View Profile
    • About energy
  • Liked: 309
  • Likes Given: 23
Re: Managing PV + battery system
« Reply #33 on: January 07, 2018, 11:52:54 PM »
From my experience, I believe that there will be in the future 3 main configurations for batteries at home.
1) V2G which would allow peak shaving. This is quite interesting because most appliances use electricity when we are at home. The main exception is the dishwasher because it dryies the dishes about 2:30 hours after it starts. Utility companies will probably charge more for high power usage once smart meters are generalized, and the V2G system will allow you not to pay the extra cost. I don’t believe that batteries’ cost would drop so much that having batteries just for that might be financially interesting.
2) batteries that are managed by the utility company. If you manage your batteries yourself, you might load them when there is a peak on the network, and unload them when energy is available. A centralized management is much smarter. Furthermore it is not possible for the utility company to share the benefits honestly between the owner of batteries for loading when price are negative, and unloading when prices are high. Having the batteries near the end user has the main advantage that is helps when there is a general peak, but also when there is a peak just on the 10 or 20 kV line going to your living area. So I believe that we will buy batteries, install them in our houses, and get some money from the utility company for that. I heard on this forum about such a project in the Orkney Islands and in Germany. Loading batteries with excess PV production is a nice concept, but it is still expensive and from a network point of view, it makes more sense (so should bring more money to the owner) to have the batteries managed according to the needs of the network.
3) In areas where the network is not so stable, batteries are used as UPS. This is already common for the IT equipment, hospitals, military... but I heart of a dentist who bought UPS to cover all his needs during at least 30 minutes.

Well, things change quite fast and I wonder what I would say next year.

numerobis

  • Grease ice
  • Posts: 837
    • View Profile
  • Liked: 16
  • Likes Given: 3
Re: Managing PV + battery system
« Reply #34 on: January 08, 2018, 02:57:44 AM »
Most cheaper dishwashers you can turn off the drying option. Expensive ones you’d need to disconnect the heating coil.

Interesting data. I wonder how I could get the same for my house.

I’m particularly interested in seeing you average 400 W or so. We do about that as well, which was so little compared to the average for our region (despite me working at home) that I thought there was a mistake.

From my calculations, that means a 4 kW solar array would have my house be net negative power. I’d still want batteries to deal with power outages: this weekend while we were away, our apartment pipes froze because with the power out, the furnace shut off. I want to prevent that when we move.

TerryM

  • First-year ice
  • Posts: 6002
    • View Profile
  • Liked: 893
  • Likes Given: 5
Re: Managing PV + battery system
« Reply #35 on: January 08, 2018, 09:01:58 AM »
numerobis
Is it possible to get any use out of solar panels during winter at your latitude?
Terry



ghoti

  • Grease ice
  • Posts: 767
    • View Profile
  • Liked: 12
  • Likes Given: 15
Re: Managing PV + battery system
« Reply #36 on: January 08, 2018, 11:27:22 PM »
numerobis
Is it possible to get any use out of solar panels during winter at your latitude?
Terry
A quick check using the ESRL NOAA Solar calculator shows Nuuk (similar latitude 64degrees north) shows daylength today of about 5 hours but with peak noon sun elevation of 4 degrees. Not lots of light available.

However, it is not a good idea to worry about winter solar power. Even at lower latitudes in Canada like Ottawa's 46 degrees N it would be a mistake to try to optimize winter gain at the expense of summer gain. On my roof my entire December PV production in a good year equals 3 average days total between May and August. Focus on optimizing when the sun is high.

numerobis

  • Grease ice
  • Posts: 837
    • View Profile
  • Liked: 16
  • Likes Given: 3
Re: Managing PV + battery system
« Reply #37 on: January 09, 2018, 07:38:10 PM »
numerobis
Is it possible to get any use out of solar panels during winter at your latitude?
Terry

According to my predictions on my roof: October, November, December, and January are all below 10% capacity factor, with many days at zero. The rest of the months are above 10%. March, April, May are the peak.

etienne

  • Nilas ice
  • Posts: 2043
    • View Profile
    • About energy
  • Liked: 309
  • Likes Given: 23
Re: Managing PV + battery system
« Reply #38 on: March 09, 2018, 10:30:23 AM »
Just some news of the houses with batteries and PV self consumption.
PV works very well. That's not a surprise, and self consumption also.
Regarding batteries, I am not so convinced.
The problem we have is that self-consumption works quite well during the winter because there is a lot of heating needed. The houses have to be heated, just like sanitary water (it also arrives colder than during the summer), and the heat pump has a lower efficiency because the cold side is colder than during the summer. We have low depth (4 to 10 meters) geothermy and water comes back around -1°C.
So we almost never have enough energy to load the battery, only on the very sunny days which is not so common this time of year.
Most of the days, the electronic of the batteries just works to keep the system online, than there are some full loading cycles to keep batteries fit... and on one site, we have the problem that the place where batteries are stored is too cold. Heating the batteries would be nonsense, but keeping them cold is also not ok.
I believe always more that batteries only make sense for load balancing of the network. When you do that, you really use them everyday, so you don't have that continuous base load  that just keeps the system online until something happens.

oren

  • First-year ice
  • Posts: 9799
    • View Profile
  • Liked: 3582
  • Likes Given: 3914
Re: Managing PV + battery system
« Reply #39 on: March 09, 2018, 01:07:22 PM »
Thanks for the interesting updates etienne. I guess the battery will do a better job in the summer, where it might fill up during the day and last through the evening and night.
Or maybe it means if you have the battery, it might pay off to install some extra PV as the battery guarantees it can be used and not wasted (in the current season at least).

etienne

  • Nilas ice
  • Posts: 2043
    • View Profile
    • About energy
  • Liked: 309
  • Likes Given: 23
Re: Managing PV + battery system
« Reply #40 on: March 09, 2018, 01:26:56 PM »
Well, PV overproduction is not really wasted because it goes on the network and hopefully reduces global CO2 emissions.
There is a lot of talk about solar and wind curtailment, but this is only because theses are the only energies that can be easily curtailed. Never heard of nuclear or coal curtailment, but there are many talks about demand-response and hydropumping storage.
River hydro could be curtailed, don't know if it is done or not.

sidd

  • First-year ice
  • Posts: 6771
    • View Profile
  • Liked: 1046
  • Likes Given: 0
Re: Managing PV + battery system
« Reply #41 on: March 09, 2018, 09:28:09 PM »
"River hydro could be curtailed, don't know if it is done or not."

It is done, but dams also have water control responsibilities which sometimes override all else.

sidd

Zythryn

  • New ice
  • Posts: 81
    • View Profile
  • Liked: 9
  • Likes Given: 47
Re: Managing PV + battery system
« Reply #42 on: April 02, 2018, 11:14:36 PM »
...
However, it is not a good idea to worry about winter solar power. Even at lower latitudes in Canada like Ottawa's 46 degrees N it would be a mistake to try to optimize winter gain at the expense of summer gain. ...

This depends upon your goal.
For our home project, we did optimize towards winter production as winter is when we use the most electricity.
Sure, for cost/kWh produced it doesn’t give the best results.
For minimizing my electric draw from the grid it worked quite well.

We also use batteries.  The primary reason was to provide power in the winter during grid outages.  We enjoy the secondary benifit of being able to use less grid energy and more of our own.